The text under discussion (new version of 625.43 in the 2026 NEC First Draft Report) is below.
Cheers, Wayne
625.43 Disconnecting Means.
EVSE and WPTE, shall be provided with one or more disconnecting means in accordance with 625.43(A) and 625.43(B).
(A) Equipment Disconnects.
For permanently connected EVSE and WPTE, a disconnecting means shall be provided and installed in a readily accessible location. If the disconnecting means is installed remote from the equipment, a plaque or directory shall be installed on the equipment denoting the location of the disconnecting means. For cord- and plug-connected EVSE and WPTE, with a rating not exceeding 60 amperes or not exceeding 150 volts to ground, the cord and plug shall be permitted to serve as the disconnecting means. The disconnecting means shall be lockable open in accordance with 110.25.
(B) Emergency Shutoff.
For permanently connected EVSE and WPTE, one or more clearly identified emergency disconnect devices or electrical disconnects shall be provided and shall meet all of the following:
Be installed in a readily accessible location in sight from the equipment
Disconnect power to all EVSE and WPTE within sight of emergency shutoff
Be marked “EVSE EMERGENCY DISCONNECT” in accordance with 110.22(A)
Be a manual reset type
Disconnect all ungrounded conductors of the circuits simultaneously from the source of supply
The disconnecting means required in accordance with 625.43(A) shall be permitted to serve as the emergency disconnect if it complies with all the requirements of 625.43(B).