625 Disconnecting Means

Status
Not open for further replies.

NTesla76

Senior Member
Location
IA
Occupation
Electrics
I may be missing something obvious here, but I have a question regarding disconnecting means for EVSE. Its a 60 amp 240 volt charger, fastened in place. 625.43 reads I don't need a disconnecting means because it's not more than 60 amps. 625.44(B) reads I need a receptacle outlet. Wouldn't the receptacle outlet be considered a disconnecting means?
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
A receptacle is only required for fast interchange of equipment. The section below states

(C) Fixed Equipment. All other equipment shall be permanently
wired and fixed in place to the supporting surface.
 