630.12 over current protection- Overcurrent protection for arc welders shall be as provided in 630.12(A) and (B). Where the values as determined by this section do not correspond to the standard ampere ratings provided in 240.6 or where the rating or setting specified results in unnecessary opening of the overcurrent device, the next higher standard rating or setting shall be permitted.
With that being said if I have a non-motor welder with an input current of 50amps and a 20% duty cycle. Calculation comes out to 22.5 conductor ampacity. So with NM cable limited to 60degree conductor ampacity one would have to use #10awg conductors. Than would I be limited to a 30amp OCPD BUT than I read 630.12b which allowed OCPD up to 200% of conductor ampacity. So with all that said I could get by with #10awg and a 50amp OCPD correct?
Before I learned about conductor ampacity and duty cycles of welders I would have just assumed slap a 50amp OCPD and some #6awg.
With that being said if I have a non-motor welder with an input current of 50amps and a 20% duty cycle. Calculation comes out to 22.5 conductor ampacity. So with NM cable limited to 60degree conductor ampacity one would have to use #10awg conductors. Than would I be limited to a 30amp OCPD BUT than I read 630.12b which allowed OCPD up to 200% of conductor ampacity. So with all that said I could get by with #10awg and a 50amp OCPD correct?