645.10 Disconnecting Means.
A means shall be provided to disconnect power to all electronic equipment in the information technology equipment room.
Am I correct? Simply installing a non fusible disconnect just before the UPS feeder conductors enter the UPS does not satisfy this article. In an emergency this disconnect will kill power to the UPS but the UPS will now provide power instead of the feed.
Shouldn't there be a "mushroom" switch located near the exit door that will disconnect the feed to the UPS and also disconnect the load conductors leaving the UPS?
Thanks for any help,
Herb in New Jersey