i was looking at a set of drawing and saw 65000a short circuit rating with load calculations...Does this mean if i have a disconnect rated for 10,000 AIC then i cant use as service disconnect? would i need a 100,000 AIC?
You need 65k, but 100k is OK as well.
its now required to install before meter can a non fused disconnect. Do they make NON fused disconnects 100k AIC or is just for Service Disconnect?
Look more carefully at documentation of the switch, it may be acceptable if certain overcurrent device (probably a fuse) is located upstream or downstream, but at 65kA that chance of finding one that works for you probably does go down.
Also if it is required by POCO and is ahead of the "service point" NEC may not necessarily apply there, this kind of makes it the POCO's problem should there ever be an issue with it, but it is typically only their technicians that will operate this switch anyway.
Look more carefully at documentation of the switch, it may be acceptable if certain overcurrent device (probably a fuse) is located upstream or downstream, but at 65kA that chance of finding one that works for you probably does go down.
Also if it is required by POCO and is ahead of the "service point" NEC may not necessarily apply there, this kind of makes it the POCO's problem should there ever be an issue with it, but it is typically only their technicians that will operate this switch anyway.
Assuming you do have to deal with it:
UL98, which is what covers disconnect switches, only allows a maximum SCCR of 10kA for an unfused switch. But what kwired said is right; many manufacturers have submitted them for series ratings with either their own specific breakers or with fuses, and that fuse or breaker can be down stream.
Well they do seem to be able to do some tasks that other electrical workers are not supposed to do, I guess the equipment knows who is operating it and responds accordingly:blink:To which we can surmise that POCO technicians are capable of withstanding arc faults or expendable![]()
Well they do seem to be able to do some tasks that other electrical workers are not supposed to do, I guess the equipment knows who is operating it and responds accordingly:blink:
That makes the huge assumption that you can't have a fault between the disconnect and the downstream OCPD.... and that fuse or breaker can be down stream. ....
just how far downstream can it be?
That makes the huge assumption that you can't have a fault between the disconnect and the downstream OCPD.
I can see POCO denying you access to the fuse compartment though (as a potential pre-meter connecting point), which could lead to interesting problems down the road.I can't imagine the PoCo refusing to connect your service because you used a fused vs a non-fused disconnect.
The switch is after the meterI can see POCO denying you access to the fuse compartment though (as a potential pre-meter connecting point), which could lead to interesting problems down the road.
An NF disconnect would not have that problem and POCO would not necessarily even want to lock the switch handle.
The switch is after the meter
Honestly, it puzzles me too, but I've seen it in project drawings and specs now 4 or 5 times in the last year, most recently this Monday. I don't know if this is coming from the utilities or from some class the consulting engineers are taking somewhere, it makes no sense. I get involved because this seems to be most prevalent in pump panel installations on things like sewage lift stations and booster pumps where this is the only thing on the service. I only see ones that involve VFDs, and VFDs have some picky requirements on up stream protection that a lot of consultants don't pay attention to either. The contractors are coming to me asking if they can just use a fused disconnect ahead of the VFDs instead of the NF version, because it kills two birds with one stone. I'm telling them to do it.That would be odd to have a non-fused switch after the meter. What would be the point of that?
Typically it would be supply to utility required non-fused meter disconnect to metering equipment to NEC required fused or breaker service disconnect.