shay.jackson
New User
- Location
- IOWA
- Occupation
- PANELS SHOP OWNER
A customer has an mcc bucket with a 1200amp adjustable breaker (480v). They will adjust this breaker down to 400amps and it has a 65ka SCCR. They want to feed a separate panel that will house 14 motor starter circuits for pumps in the field. They say they don't want a main breaker in the panel, just a disconnect. from there we are going to distribution blocks, then breakers (not mpcb to achieve the 65ka) then to the starters/overloads. The starters have a 10ka SCCR. to avoid my panel having a 10ka SCCR, My UL rep told me that the way to do this is to series protect the starter with a fused terminal rated at 65ka peak let through, then the breakers rated at 65ka peak let through, then the starters for every branch.
I have never seen this done and i have the following questions.
1. How would sizing be done to ensure they are coordinated to trip in the correct sequence based on the fault current?
2. If i used a main breaker as a disconnect that was rated for 65ka SCCR would i still need the fuses at all?
Thank you for you time
I have never seen this done and i have the following questions.
1. How would sizing be done to ensure they are coordinated to trip in the correct sequence based on the fault current?
2. If i used a main breaker as a disconnect that was rated for 65ka SCCR would i still need the fuses at all?