bluecollar84
- US
Would anyone consider this pool equipment situation a corrosive environment per NEC article 680.14 ?
Are you familiar with 680.14 ?
Seems clear cut as falling under 2017's new section 680.14: "open areas under decks adjacent to or abutting the pool structure."Would anyone consider this pool equipment situation a corrosive environment per NEC article 680.14 ?
Cheers, Wayne
Ouch. Time to pony up and buy this I guess.
680.14 Corrosive Environment.
(A) General. Areas where pool sanitation chemicals are
stored, as well as areas with circulation pumps, automatic chlorinators,
filters, open areas under decks adjacent to or abutting
the pool structure, and similar locations shall be considered to
be a corrosive environment. The air in such areas shall be
considered to be laden with acid, chlorine, and bromine
vapors, or any combination of acid, chlorine, or bromine
vapors, and any liquids or condensation in those areas shall be
considered to be laden with acids, chlorine, and bromine
vapors.
(B) Wiring Methods. Wiring methods in the areas described
in 680.14(A) shall be listed and identified for use in such areas.
Rigid metal conduit, intermediate metal conduit, rigid polyvinyl
chloride conduit, and reinforced thermosetting resin
conduit shall be considered to be resistant to the corrosive
environment specified in 680.14(A).
This pool is a salt pool does that change anything ?