A swimming pool I wired failed its final last week. The inspector said I needed a receptacle at least 10' from the pool, but not more than 20'. She cited section 680.6 1 & 2. I think she meant 680.22 (3).
There is a receptacle 24' from the pool at the control equiptment and a receptacle 26' from the pool for a fountain.
The HO doesn't want any receptacles near his pool. What is the intent of this code? Why does he need a receptacle so close to the pool?
The pool contractor used rebar tie wire to bond all of the equiptment together and terminated all of the bond wires on one ground rod clamp. The inspector had nothing to say about this. The sub panel for the pool is an Intellitouch 50 amp panel.