Only my 2nd above ground pool! (48")
I understand since it's 48" it is considered permanent and I'm familiar with all of the bonding... pump, water, copper ring 18"-24" around the pool etc...
I'm trying to determine when a standard 120V (Straight blade) configuration is permitted for the pump receptacle and when a twist-lock is required.
To me, it looks like 680.22 (A)(1) permits the standard configuration only if the receptacle is at least 10Ft from the pool but it requires the twist lock if it's within 6-10Ft.
Is the distance from the pool the only deciding factor? (I will be installing a GFCI circuit breaker)
AHJ is on 2011 NEC
I understand since it's 48" it is considered permanent and I'm familiar with all of the bonding... pump, water, copper ring 18"-24" around the pool etc...
I'm trying to determine when a standard 120V (Straight blade) configuration is permitted for the pump receptacle and when a twist-lock is required.
To me, it looks like 680.22 (A)(1) permits the standard configuration only if the receptacle is at least 10Ft from the pool but it requires the twist lock if it's within 6-10Ft.
Is the distance from the pool the only deciding factor? (I will be installing a GFCI circuit breaker)
AHJ is on 2011 NEC