680.22(A)(4) GFCI Protection.

All 15- and 20-ampere, single-phase, 125-volt receptacles located within 6.0 m (20 ft) of the inside walls of a pool shall be protected by a ground-fault circuit interrupter.
I'm looking for the exception that says receptacles located within the house but within 20' of the pool do not require GFCI protection.

Thanks
 
Last edited by a moderator:
Also, whats wrong with the software here that wont let you put a capital letter in ( ) in the thread title???
 