brantmacga
Señor Member
- Georgia
- Former Child
I have a friend that builds pools; he happened to build one for a customer of our service dept.
I was there to troubleshoot an issue the homeowner said started after the pool was installed, and they asked me to look at the pool panel; the issue was completely unrelated.
I noticed the pool electrician used a QO230GFI for the pool feeder, and an HOM120 for the 120v pool light.
I mentioned 680.23(A)(3) to my friend, which requires the GFI for the pool light be installed in the branch circuit so that he is covered from a liability standpoint.
My question is, why is this a specific requirement? Why would the feeder GFI not be sufficient? My only guess is that maybe the CMP felt that you could end up with a circuit path longer than 250', which seems to be longer than what manufacturers recommend, although I've only seen that this can cause "nuisance tripping" in documentation. The particular install I looked at, the light was probably close to 200' from the feeder GFI.
Any other thoughts? Is this something worth looking into making a submission for revision?
We also do quite a bit of pool work, but install branch circuit GFI's where required as everyone is using automated panels and do not want a tripped GFI shutting down the whole system. Most of our installs are also above 50A anyway.
Thanks
Thanks