Senior Member
680.23(A)(5) limits the MINIMUM depth that an underwater luminaire may be installed at 18" (4" if listed for that depth) below the normal water level of a pool.
680.23(B)(6) adds further requirements (without specific limits) on the MAXIMUM depth below the normal water level. It states, "Luminaires shall be installed in such a manner that personnel can reach the lumiaire for relamping, maintenance, or inspection while on the deck or equivalently dry location."
We, as a jurisdiction are using 24" below the normal water level to the center of the luminaire as a maximum (based on average(?) arm length).
We have a contractor wishing to install a custom pool with a side spa. The wet niche fixture to be installed in the spa is shown in the face of the lowest "step" in the spa. This would put the center of the luminaire at approximately 36" below the normal water level in the spa. (this spa is part of the custom pool, not self-contained). (680.43(B)(2) states that underwater luminaires in spas shall comply with 680.23 or 680.33)
Has anyone dealt with this code issue as yet? This article (680.23(B)(6)) IS new in the 2005 NEC. We are on the 2007 California Electrical Code, which is basically the 2005 NEC as written (the only one CA did like that!). I was not able to find any threads on the subject. Any input or insight would be helpful for us to properly enforce this code.
680.23(B)(6) adds further requirements (without specific limits) on the MAXIMUM depth below the normal water level. It states, "Luminaires shall be installed in such a manner that personnel can reach the lumiaire for relamping, maintenance, or inspection while on the deck or equivalently dry location."
We, as a jurisdiction are using 24" below the normal water level to the center of the luminaire as a maximum (based on average(?) arm length).
We have a contractor wishing to install a custom pool with a side spa. The wet niche fixture to be installed in the spa is shown in the face of the lowest "step" in the spa. This would put the center of the luminaire at approximately 36" below the normal water level in the spa. (this spa is part of the custom pool, not self-contained). (680.43(B)(2) states that underwater luminaires in spas shall comply with 680.23 or 680.33)
Has anyone dealt with this code issue as yet? This article (680.23(B)(6)) IS new in the 2005 NEC. We are on the 2007 California Electrical Code, which is basically the 2005 NEC as written (the only one CA did like that!). I was not able to find any threads on the subject. Any input or insight would be helpful for us to properly enforce this code.