680.23(B)(2) states "conduit shall be installed from the forming shell to a junction box or other enclosure conforming to the requirements in 680.24. Now without typing the whole thing out says 680.24(A)(1)(1) says be equipped with threaded entries or hubs or a nonmetallic hub. Well I did two pool that the cord was long enough that I could take it all the way back where where the pool light transformer was located. So instead of placing a junction box and having to spice I just took the cord to the transformer box and use a plastic sealite fitting. The cord was in PVC from the wet-niche and I just transition from PVC to sealite. Well one inspector failed it stating 680.24 and the other inspector passed the other job. Which is it? Do we need a junction box or not.