680.23(F)(1) and (2)

Status
Not open for further replies.

chris kennedy

Senior Member
Location
Miami Fla.
Occupation
60 yr old tool twisting electrician
Pool light branch circuit is run underground in PVC to WP j-box on the side of a dwelling unit with other branch circuit. The conductors for the pool light nipple into and approved tranny while the other change to NM and enter the house. Can I intercept the ungrounded conductor of the pool light circuit and run NM to a switch inside the house. An insulated EGC compliant with the title section will be run from panel to tranny/deck box. The switch NM EGC will be tied into the EGC run for the other branch circuits.

Thanks
 
And then this one for a different take

subscribed.gif
Inspector Requires MC for Pool Transformer in Single Family House
 
Status
Not open for further replies.