680.23(F)(3) Conductors. Conductors on the load side of a groundfault
circuit interrupter or of a transformer, used to comply
with the provisions of 680.23(A)(8), shall not occupy raceways,
boxes, or enclosures containing other conductors unless
one of the following conditions applies:
(1) The other conductors are protected by ground-fault circuit
interrupters.
(2) The other conductors are grounding conductors.
(3) The other conductors are supply conductors to a feedthrough-
type ground-fault circuit interrupter.
(4) Ground-fault circuit interrupters shall be permitted in a
panelboard that contains circuits protected by other
than ground-fault circuit interrupters.