680.25 (A) (1) Pool Feeders

Status
Not open for further replies.

E16

Member
Location
Iowa
Occupation
Electrical Contractor
I need some help on which feeders need to be in conduit per 680.25 (A) (1)?
I feel that the feeder from the 150 amp breaker in the meter to the Pool house panel and then from the Pool house panel to the Pool equipment panel should all be in conduit.

I have attached a drawing for refernce.

Thanks for the help
 

Attachments

  • pool feeder drawing.pdf
    16.4 KB · Views: 0
Yes.
The feeder from the 150 amp breaker in the meter to the Pool house panel and then from the Pool house panel to the Pool equipment panel should all be in conduit.
 
Can some one help me with the reasoning of why the feeders need to be in conduit.
I understand that this needs to happen but just trying to understand the reason.

Thanks
 
Can some one help me with the reasoning of why the feeders need to be in conduit.
I understand that this needs to happen but just trying to understand the reason.

Thanks

The ground wire needs to be insulated, although that alone doesnt explain excluding something like direct burial MC cable. The other part is probably protection from physical damage. Jess Guessin'.
 