680.43(D) eliminates 680.26?

Status
Not open for further replies.

George Stolz

Moderator
Staff member
Location
Windsor, CO NEC: 2017
Occupation
Service Manager
I have it locked in my head that a hot tub installed indoors need not worry about complying with 680.26. I am at the underground stage of an indoor hot tub installation, and decided to take a closer look at Article 680, Part III to be sure that I wasn't missing anything, and now I am confused.

According to what I remember, 680.26 is required in outdoor hot tub installations, but not indoors. However, looking at 680.42 and .43 I'm not seeing the difference.

Looking back to the ROP leading to the 2005 NEC, the CMP appears to believe the words say the same thing I thought, but I don't see how the words support that conclusion. As I sit here and read the 2008 NEC now, it appears that an equipotential bonding grid and bonding the pool water would be required in an indoor pool. Is that incorrect, and why?
 
But 680.42(B) does not say "Hot Tubs installed outdoors shall be installed according to the provisions of 680.26, sans the staves requirement." It says that something is not bonded as it would be required in 680.26. It would be nice if it were more direct, IMO.
 