physis
Senior Member
WARNING
Don't be intimidated by the length. It's only because the same terminology issue repeatedly appears in the two sections and their subsections. A lot of the proposed revisions are very similar.
Italics: Deleted text.
Bold italics: New text.
(a) and (b) are footnotes
______________________________________________________________________________________________
______________________________________________________________________________________________
Revise sections 690.13 and 690.14. Overview:
The objective of the proposal is to clarify what sections of the solar photovoltaic system are addressed by the disconnecting means requirements in sections 690.13 and 690.14. Each proposed revision is intended to clarify the same issue. That is that the disconnecting means is required to do only one thing. Disconnect the photovoltaic power source at the photovoltaic output circuit.
There are five different terms used in reference to the photovoltaic side of the disconnecting means.
</font>
The other three terms look very similar to terms that are defined in section 690.2. Obviously those definitions are not intended to describe the similar terms. Yet someone needing a definition might have a strong inclination to assume, because of the similarity of terms and lack of a definition corresponding to the actual term, that the wrong definition should be used.
Probably the most troubling example is the use of the two undefined terms:
</font>
</font>
The proposed revisions are intended to better organize the terminology by reducing the use of ildefined language.
______________________________________________________________________________________________
Add Definition In Section 690.2:
Photovoltaic Array. A photovoltaic array is an array as defined in this section also including any additional components such as source circuit isolating switches, overcurrent devices, and blocking diodes, up to and including the photovoltaic output circuit conductors.
Substantiation:
There are simply too many instances of the terminology used in reference to system components on both sides of the disconnecting means required by sections 690.13 and 690.14 changing from one subsection to the next while the subject and the components of the system are the same. The terms used should be consistent and defined. The proposed term, photovoltaic array, and it?s definition accomplish both.
______________________________________________________________________________________________
Revise Definition of Array In Section 690.2
Array. A mechanically integrated assembly of one or more modules or panels with a support structure and foundation, tracker, and other components, as required, to form a direct-current power-producing unit.
Substantiation:
The proposed revisions to sections 690.13 and 690.14 will identify the disconnecting means covered in those sections as the photovoltaic array disconnecting means. The current definition of array doesn?t include an assembly having only one module or panel. Therefore the proposed term, photovoltaic array, could be interpreted as excluding a single module or single panel assembly. Additionally, a single module or panel array is possible and should be within the definition of array.
______________________________________________________________________________________________
Revise Section 690.13.
III Disconnecting Means
690.13 All Conductors. Means shall be provided to disconnect all current-carrying conductors of a photovoltaic power source from all other conductors in a building or other structure. Where a circuit grounding conductor is not designed to be automatically interrupted as part of a ground fault protection system required by 690.5, a switch or circuit breaker used as a disconnecting means shall not have a pole in the grounded conductor.
690.13 All Photovoltaic Array Conductors. Means shall be provided to disconnect all current-carrying conductors of all photovoltaic arrays from all (a) other conductors in a building or other structure. Where a circuit grounding conductor is not designed to be automatically interrupted as part of a ground fault protection system required by 690.5, a switch or circuit breaker used as a disconnecting means shall not have (b) a pole in the grounded conductor.
Substantiation:
In the interest of consistency the existing term, photovoltaic power source, should be replaced with the proposed term, photovoltaic arrays.
(a) This should refer to premises wiring but in order to revise the language in this section the definition of premises wiring in article 100 will also need to be revised where it refers to photovoltaic systems. I haven?t decided whether I want to address that as well and I'm interested in input.
(b) ?A pole in the grounded conductor? is bizarre language. I want to change it but I?m not sure it doesn?t mean something I?m not aware of.
______________________________________________________________________________________________
Revise Section:
690.14 Additional Provisions. Photovoltaic disconnecting means shall comply with 690.14(A) through (C).
690.14 Additional Provisions. Photovoltaic array disconnecting means shall comply with 690.14(A) through (C).
Substantiation:
The term photovoltaic is vague and can be associated with any part of the solar photovoltaic system or the entire system. It should be replaced with the proposed term photovoltaic array.
______________________________________________________________________________________________
Revise Subsection:
690.14(B) Equipment. Equipment such as photovoltaic source circuit isolating switches, overcurrent devices, and blocking diodes shall be permitted on the photovoltaic side of the photovoltaic disconnecting means.
690.14(B) Equipment. Equipment such as photovoltaic source circuit isolating switches, overcurrent devices, and blocking diodes shall be permitted on the photovoltaic array side of the photovoltaic array disconnecting means.
Substantiation:
The term photovoltaic is vague and can be associated with any part of the solar photovoltaic system or the entire system. It should be replaced with the proposed term photovoltaic array.
______________________________________________________________________________________________
Delete or Revise Subsection:
690.14(C) Requirements for Disconnecting Means. Means shall be provided to disconnect all conductors in a building or other structure from the photovoltaic system conductors.
690.14(C) Requirements for Disconnecting Means. Means shall be provided to disconnect all conductors in a building or other structure (a) from the photovoltaic output circuit conductors.
Substantiation:
690.14(C) is redundant. It is the same requirement as 690.13. It should be deleted. If it is not deleted, the existing undefined term, photovoltaic system conductors, should be replaced with the proposed term, photovoltaic output circuit conductors. Partly because of the definition for solar photovoltaic system in section 690.2 the term photovoltaic system conductors can be misinterpreted as referring to the inverter output circuit.
(This substantiation needs some work)
______________________________________________________________________________________________
Revise Subsection:
690.14(C)(1) Location. The photovoltaic disconnecting means shall be installed at a readily accessible location either outside of a building or structure or inside nearest the point of entry of the system conductors. The photovoltaic system disconnecting means shall not be installed in bathrooms.
690.14(C)(1) Location. The photovoltaic array disconnecting means shall be installed at a readily accessible location either outside of a building or structure or inside nearest the point of entry of the photovoltaic output circuit conductors. The photovoltaic array disconnecting means shall not be installed in bathrooms.
Substantiation:
The existing terms are not defined and there are corresponding terms that have definitions in 690.2. Those terms along with the proposed term, photovoltaic array, should be used in their place.
______________________________________________________________________________________________
______________________________________________________________________________________________
All that's left is 690.14(C)(2) through (5). I thought I'd get some input before revising the rest of the book.
______________________________________________________________________________________________
I'm also interested in ideas for other kinds of supporting substantiation.
I'm really not completely happy with the term photovoltaic array and it's definition. Other ideas for a better term or a different way to deal with it, like focusing on the output conductors instead, are encouraged. What I do like about it is that with regard to the disconnect it plainly describes disconnecting the solar cells.
I'm also interested in any insights as to why essentially the same thing is being said so many different ways. I want to try to not overlook the CMP's reasons for doing this that might not be so obvious.
[ July 18, 2005, 03:31 PM: Message edited by: physis ]
Don't be intimidated by the length. It's only because the same terminology issue repeatedly appears in the two sections and their subsections. A lot of the proposed revisions are very similar.
Italics: Deleted text.
Bold italics: New text.
(a) and (b) are footnotes
______________________________________________________________________________________________
______________________________________________________________________________________________
Revise sections 690.13 and 690.14. Overview:
The objective of the proposal is to clarify what sections of the solar photovoltaic system are addressed by the disconnecting means requirements in sections 690.13 and 690.14. Each proposed revision is intended to clarify the same issue. That is that the disconnecting means is required to do only one thing. Disconnect the photovoltaic power source at the photovoltaic output circuit.
There are five different terms used in reference to the photovoltaic side of the disconnecting means.
</font>
- <font size="2" face="Verdana, Helvetica, sans-serif">Photovoltaic Power Source</font>
- <font size="2" face="Verdana, Helvetica, sans-serif">Photovoltaic System</font>
- <font size="2" face="Verdana, Helvetica, sans-serif">Photovoltaic System Conductors</font>
- <font size="2" face="Verdana, Helvetica, sans-serif">Photovoltaic Source Circuit</font>
- <font size="2" face="Verdana, Helvetica, sans-serif">System Conductors</font>
The other three terms look very similar to terms that are defined in section 690.2. Obviously those definitions are not intended to describe the similar terms. Yet someone needing a definition might have a strong inclination to assume, because of the similarity of terms and lack of a definition corresponding to the actual term, that the wrong definition should be used.
Probably the most troubling example is the use of the two undefined terms:
</font>
- <font size="2" face="Verdana, Helvetica, sans-serif">Photovoltaic system</font>
- <font size="2" face="Verdana, Helvetica, sans-serif">Photovoltaic system conductors</font>
</font>
- <font size="2" face="Verdana, Helvetica, sans-serif">Solar photovoltaic system</font>
The proposed revisions are intended to better organize the terminology by reducing the use of ildefined language.
______________________________________________________________________________________________
Add Definition In Section 690.2:
Photovoltaic Array. A photovoltaic array is an array as defined in this section also including any additional components such as source circuit isolating switches, overcurrent devices, and blocking diodes, up to and including the photovoltaic output circuit conductors.
Substantiation:
There are simply too many instances of the terminology used in reference to system components on both sides of the disconnecting means required by sections 690.13 and 690.14 changing from one subsection to the next while the subject and the components of the system are the same. The terms used should be consistent and defined. The proposed term, photovoltaic array, and it?s definition accomplish both.
______________________________________________________________________________________________
Revise Definition of Array In Section 690.2
Array. A mechanically integrated assembly of one or more modules or panels with a support structure and foundation, tracker, and other components, as required, to form a direct-current power-producing unit.
Substantiation:
The proposed revisions to sections 690.13 and 690.14 will identify the disconnecting means covered in those sections as the photovoltaic array disconnecting means. The current definition of array doesn?t include an assembly having only one module or panel. Therefore the proposed term, photovoltaic array, could be interpreted as excluding a single module or single panel assembly. Additionally, a single module or panel array is possible and should be within the definition of array.
______________________________________________________________________________________________
Revise Section 690.13.
III Disconnecting Means
690.13 All Conductors. Means shall be provided to disconnect all current-carrying conductors of a photovoltaic power source from all other conductors in a building or other structure. Where a circuit grounding conductor is not designed to be automatically interrupted as part of a ground fault protection system required by 690.5, a switch or circuit breaker used as a disconnecting means shall not have a pole in the grounded conductor.
690.13 All Photovoltaic Array Conductors. Means shall be provided to disconnect all current-carrying conductors of all photovoltaic arrays from all (a) other conductors in a building or other structure. Where a circuit grounding conductor is not designed to be automatically interrupted as part of a ground fault protection system required by 690.5, a switch or circuit breaker used as a disconnecting means shall not have (b) a pole in the grounded conductor.
Substantiation:
In the interest of consistency the existing term, photovoltaic power source, should be replaced with the proposed term, photovoltaic arrays.
(a) This should refer to premises wiring but in order to revise the language in this section the definition of premises wiring in article 100 will also need to be revised where it refers to photovoltaic systems. I haven?t decided whether I want to address that as well and I'm interested in input.
(b) ?A pole in the grounded conductor? is bizarre language. I want to change it but I?m not sure it doesn?t mean something I?m not aware of.
______________________________________________________________________________________________
Revise Section:
690.14 Additional Provisions. Photovoltaic disconnecting means shall comply with 690.14(A) through (C).
690.14 Additional Provisions. Photovoltaic array disconnecting means shall comply with 690.14(A) through (C).
Substantiation:
The term photovoltaic is vague and can be associated with any part of the solar photovoltaic system or the entire system. It should be replaced with the proposed term photovoltaic array.
______________________________________________________________________________________________
Revise Subsection:
690.14(B) Equipment. Equipment such as photovoltaic source circuit isolating switches, overcurrent devices, and blocking diodes shall be permitted on the photovoltaic side of the photovoltaic disconnecting means.
690.14(B) Equipment. Equipment such as photovoltaic source circuit isolating switches, overcurrent devices, and blocking diodes shall be permitted on the photovoltaic array side of the photovoltaic array disconnecting means.
Substantiation:
The term photovoltaic is vague and can be associated with any part of the solar photovoltaic system or the entire system. It should be replaced with the proposed term photovoltaic array.
______________________________________________________________________________________________
Delete or Revise Subsection:
690.14(C) Requirements for Disconnecting Means. Means shall be provided to disconnect all conductors in a building or other structure from the photovoltaic system conductors.
690.14(C) Requirements for Disconnecting Means. Means shall be provided to disconnect all conductors in a building or other structure (a) from the photovoltaic output circuit conductors.
Substantiation:
690.14(C) is redundant. It is the same requirement as 690.13. It should be deleted. If it is not deleted, the existing undefined term, photovoltaic system conductors, should be replaced with the proposed term, photovoltaic output circuit conductors. Partly because of the definition for solar photovoltaic system in section 690.2 the term photovoltaic system conductors can be misinterpreted as referring to the inverter output circuit.
(This substantiation needs some work)
______________________________________________________________________________________________
Revise Subsection:
690.14(C)(1) Location. The photovoltaic disconnecting means shall be installed at a readily accessible location either outside of a building or structure or inside nearest the point of entry of the system conductors. The photovoltaic system disconnecting means shall not be installed in bathrooms.
690.14(C)(1) Location. The photovoltaic array disconnecting means shall be installed at a readily accessible location either outside of a building or structure or inside nearest the point of entry of the photovoltaic output circuit conductors. The photovoltaic array disconnecting means shall not be installed in bathrooms.
Substantiation:
The existing terms are not defined and there are corresponding terms that have definitions in 690.2. Those terms along with the proposed term, photovoltaic array, should be used in their place.
______________________________________________________________________________________________
______________________________________________________________________________________________
All that's left is 690.14(C)(2) through (5). I thought I'd get some input before revising the rest of the book.
______________________________________________________________________________________________
I'm also interested in ideas for other kinds of supporting substantiation.
I'm really not completely happy with the term photovoltaic array and it's definition. Other ideas for a better term or a different way to deal with it, like focusing on the output conductors instead, are encouraged. What I do like about it is that with regard to the disconnect it plainly describes disconnecting the solar cells.
I'm also interested in any insights as to why essentially the same thing is being said so many different ways. I want to try to not overlook the CMP's reasons for doing this that might not be so obvious.