Denver inspector
Member
- Location
- Denver , Colorado
690.31 ( E ) States the wiring methode shall comply with aditional requirement of 1- 4 of 690.31.
There has been some discussion of weather or not this requirement pertains to the conduit system on the exterrior of a residence from a Solar System Installer.
690.31 ( E ) ( 3 ) (1) States that exposed raceway and other wiring methods , Shall be marked .
The Question arises does this only pertain to the inside of the structure as stated in the main body or does the inclusion of the verbage ( from the point of penetration of the structure to the first readily accessible disconnecting means ) imply that all conduit system from the roof to the first dissconnect reqquire marking?????
I have been asked to present this Question to the forum for review.
I await your response.
There has been some discussion of weather or not this requirement pertains to the conduit system on the exterrior of a residence from a Solar System Installer.
690.31 ( E ) ( 3 ) (1) States that exposed raceway and other wiring methods , Shall be marked .
The Question arises does this only pertain to the inside of the structure as stated in the main body or does the inclusion of the verbage ( from the point of penetration of the structure to the first readily accessible disconnecting means ) imply that all conduit system from the roof to the first dissconnect reqquire marking?????