This question is based on the 2017 NEC and is similar this previous post.
Is there a requirement to run an EGC from a solar array back to the main service? The racking system we use is UL 2703 listed to bond all the metal parts together, we drive (2) of the supporting pipes 8' deep to meet the requirement of 250.52(5)(a), and the inverter back at the house is ungrounded.
It seems like this method adheres to both the spirit (effective ground fault path) and the letter of the NEC since it bonds the modules per 690.43(A), bonds the racking per 690.43(B), leaves with the circuit conductors per 690.43(C) (albeit gets to where it's going much faster), and complies with 250.134 per 250.134(B) Exception #2. Any other requirements I might be missing?
Regards,
Barklie Estes
Is there a requirement to run an EGC from a solar array back to the main service? The racking system we use is UL 2703 listed to bond all the metal parts together, we drive (2) of the supporting pipes 8' deep to meet the requirement of 250.52(5)(a), and the inverter back at the house is ungrounded.
It seems like this method adheres to both the spirit (effective ground fault path) and the letter of the NEC since it bonds the modules per 690.43(A), bonds the racking per 690.43(B), leaves with the circuit conductors per 690.43(C) (albeit gets to where it's going much faster), and complies with 250.134 per 250.134(B) Exception #2. Any other requirements I might be missing?
Regards,
Barklie Estes