690.46 and EGC Sizing

Status
Not open for further replies.

philn

Member
Location
California
Occupation
Product Manager
Why was 690.46, which references 250.120(C), removed in NEC 2020? We've seen instances where plans are approved with #8 EGCs at the array. Are AHJs simply not enforcing 250.120(C), or do they consider EGC at the array under rooftop panels to be sufficiently protected?
 
I would think they consider the grounding conductors along with the string conductors under the modules protected from physical damage.
 
Yay, it's gone.

I can't find any reference to why in the 2020 revision info.

Out of a couple dozen jurisdictions I've worked in, only two or three enforced it for residential rooftop arrays.
 