690.47 (c) (3)

Status
Not open for further replies.
PV Grounding and Bonding

PV Grounding and Bonding

It is hard to explain the various pieces, and they changed over the years.

If you are needing to understand grid connected PV inverter systems I suggest the following Arizona Public Service (APS) sample system design (see the 3-line diagram for grounding details):

http://www.aps.com/_files/SolarRenewable/AllDiagramsSampleNonRes.pdf?source=dg

Other resources:
http://www.aps.com/main/green/choice/choice_79.html

I generally use a #6 equipment grounding conductor rather than the minimum #8 because it needs less protection. The utilities in Arizona insist on the equipment grounding conductor running from the inverter to the main grounding conductor, bypassing their expensive bi-directional digital KWH meter. However, the utilities are paying substantial rebates.
 