eventhorizons
Member
- Location
- Barstow, CA USA
Customer's existing setup consists of a 200A 3-phase Service meter with a 200A fused disconnect immediately adjacent to it. From the disconnect, it penetrates the building and goes to a 200A panel with a main breaker. 4/0 wire for all.
We are installing a solar array on the roof that will supply a peak of 42A. The original intention was to use the "10-foot Feeder tap rule" and tap between the outside fuses and the inside breaker, installing a 100A disconnect with 60A fuses. All panels are immediately next to each other.
Meter <----> 200A Fused Disconnect <----Tap----> 200A MB panel
Tap <--------> 60A-fused source
The county plan-checker rejected that idea, saying that 690.64(B)(2) applied here. This required changing the plan such that we would instead add a 200A panel and run 4/0 wire, making it a "splice" instead of a "tap" and also downsizing the main meter source to 175A. The customer does not need the full 200A service, so this is not a problem for him.
Question: Is the checker applying the code correctly? Based on my detail reading, especially the articles by John Wiles, I feel that he is. But this is one of the situations that begs for an exception, since the INTENT of the rule is to prevent overload of the conductors/bus due to multiple sources. In this case, there is no way that the current in the conductors can exceed 200A.
Thanks in advance for your feedback.
Ken
We are installing a solar array on the roof that will supply a peak of 42A. The original intention was to use the "10-foot Feeder tap rule" and tap between the outside fuses and the inside breaker, installing a 100A disconnect with 60A fuses. All panels are immediately next to each other.
Meter <----> 200A Fused Disconnect <----Tap----> 200A MB panel
Tap <--------> 60A-fused source
The county plan-checker rejected that idea, saying that 690.64(B)(2) applied here. This required changing the plan such that we would instead add a 200A panel and run 4/0 wire, making it a "splice" instead of a "tap" and also downsizing the main meter source to 175A. The customer does not need the full 200A service, so this is not a problem for him.
Question: Is the checker applying the code correctly? Based on my detail reading, especially the articles by John Wiles, I feel that he is. But this is one of the situations that begs for an exception, since the INTENT of the rule is to prevent overload of the conductors/bus due to multiple sources. In this case, there is no way that the current in the conductors can exceed 200A.
Thanks in advance for your feedback.
Ken