Re-reading section 695.4A for the 100th time and I have come to the conclusion that it allows a direct service connection to the fire pump controller without any overcurrent protection or disconnecting means within the fire pump controller or anywhere else. I checked the definition of fire pump controller in NFPA 20 and nowhere does it state for the controller to come equipped with OCPD or disconnect. Also NFPA 20 9.2.3 states no more than one disconnecting means is allowed in the supply circuit to the fire pump controller. NFPA 20 9.2.3 isn't stating an OCPD or disconnect switch is required; just that if you do install one, you can only have one.
Need a sanity check. Thoughts?
Also, I have noticed the OCPD integral with fire pump controllers are not rated for the locked rotor amps butt are typically sized for 125% for FLA. How are they allowed to size for 125% and not 600% (or LRA)?
Thanks.
Need a sanity check. Thoughts?
Also, I have noticed the OCPD integral with fire pump controllers are not rated for the locked rotor amps butt are typically sized for 125% for FLA. How are they allowed to size for 125% and not 600% (or LRA)?
Thanks.