695.7 Exception

Status
Not open for further replies.

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Semi-Retired Electrical Engineer
Can anyone interpret this for me? I can't make any sense out of "emergency run mechanical starting."
 

Buck Parrish

Senior Member
Location
NC & IN
You know the Handbook usually emphasizes something they think people may have a hard time with.

Well they, too did not write any thing extra other then the code's exception. Perhaps they weren't sure either.

I'll give it a go. Emergency Running pump could be a fire pump that is supplying sprinklers in a building . It is started mechanically say from a heat detector.
 

Hv&Lv

Senior Member
Location
-
Occupation
Engineer/Technician
Can anyone interpret this for me? I can't make any sense out of "emergency run mechanical starting."
Say you need the pump in an emergency. The control circuit fails. There is an emergency start handle on the pumps That is independent of control circuits or other control devices.
 

texie

Senior Member
Location
Fort Collins, Colorado
Occupation
Electrician, Contractor, Inspector
As Hv&Lv said, this is a mechanical handle to force the contactor closed. Similar to a mechanical handle on an ATS. The voltage drop requirement does not apply when started in this manner.
 
Last edited:

Buck Parrish

Senior Member
Location
NC & IN
Charlie, or any body, In this exception, would it make sense to use the word "manual" and not "mechanical" As ''mechanical can be used for an automatic or a manual system.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
Charlie, or any body, In this exception, would it make sense to use the word "manual" and not "mechanical" As ''mechanical can be used for an automatic or a manual system.
In my opinion, no. "Manual" merely implies "requires human intervention," while "mechanical" implies "no power required."
 

texie

Senior Member
Location
Fort Collins, Colorado
Occupation
Electrician, Contractor, Inspector
In my opinion, no. "Manual" merely implies "requires human intervention," while "mechanical" implies "no power required."
Yes and a good example of this is with transfer switches. You can get manual mechanical transfer switches or (in larger sizes) you can get non-automatic that are controlled electrically.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Charlie, or any body, In this exception, would it make sense to use the word "manual" and not "mechanical" As ''mechanical can be used for an automatic or a manual system.
The " [20:9.4.2] " after the exception indicates that it is extracted material from NFPA 20. It is not permitted to be modified by the NEC technical committee when it is extracted from NFPA 20 and inserted into the NEC. Any change has to be made by a PI submitted to the technical committee for NFPA 20.
 