Can anyone interpret this for me? I can't make any sense out of "emergency run mechanical starting."
Say you need the pump in an emergency. The control circuit fails. There is an emergency start handle on the pumps That is independent of control circuits or other control devices.Can anyone interpret this for me? I can't make any sense out of "emergency run mechanical starting."
In my opinion, no. "Manual" merely implies "requires human intervention," while "mechanical" implies "no power required."Charlie, or any body, In this exception, would it make sense to use the word "manual" and not "mechanical" As ''mechanical can be used for an automatic or a manual system.
Yes and a good example of this is with transfer switches. You can get manual mechanical transfer switches or (in larger sizes) you can get non-automatic that are controlled electrically.In my opinion, no. "Manual" merely implies "requires human intervention," while "mechanical" implies "no power required."
The " [20:9.4.2] " after the exception indicates that it is extracted material from NFPA 20. It is not permitted to be modified by the NEC technical committee when it is extracted from NFPA 20 and inserted into the NEC. Any change has to be made by a PI submitted to the technical committee for NFPA 20.Charlie, or any body, In this exception, would it make sense to use the word "manual" and not "mechanical" As ''mechanical can be used for an automatic or a manual system.