Can anyone interpret this for me? I can't make any sense out of "emergency run mechanical starting."
 
You know the Handbook usually emphasizes something they think people may have a hard time with.

Well they, too did not write any thing extra other then the code's exception. Perhaps they weren't sure either.

I'll give it a go. Emergency Running pump could be a fire pump that is supplying sprinklers in a building . It is started mechanically say from a heat detector.
 
Can anyone interpret this for me? I can't make any sense out of "emergency run mechanical starting."
Say you need the pump in an emergency. The control circuit fails. There is an emergency start handle on the pumps That is independent of control circuits or other control devices.
 
As Hv&Lv said, this is a mechanical handle to force the contactor closed. Similar to a mechanical handle on an ATS. The voltage drop requirement does not apply when started in this manner.
 
Last edited:
Charlie, or any body, In this exception, would it make sense to use the word "manual" and not "mechanical" As ''mechanical can be used for an automatic or a manual system.
 
Charlie, or any body, In this exception, would it make sense to use the word "manual" and not "mechanical" As ''mechanical can be used for an automatic or a manual system.
In my opinion, no. "Manual" merely implies "requires human intervention," while "mechanical" implies "no power required."
 
In my opinion, no. "Manual" merely implies "requires human intervention," while "mechanical" implies "no power required."
Yes and a good example of this is with transfer switches. You can get manual mechanical transfer switches or (in larger sizes) you can get non-automatic that are controlled electrically.
 
Charlie, or any body, In this exception, would it make sense to use the word "manual" and not "mechanical" As ''mechanical can be used for an automatic or a manual system.
The " [20:9.4.2] " after the exception indicates that it is extracted material from NFPA 20. It is not permitted to be modified by the NEC technical committee when it is extracted from NFPA 20 and inserted into the NEC. Any change has to be made by a PI submitted to the technical committee for NFPA 20.
 