695 fire pumps

Status
Not open for further replies.

BArmy

Member
Location
Jackson Wy
Occupation
inspector
Question on Art 695. Does 695.12(D) refer to only fire pump equipment or does the minimum height include wall heaters? Also 695.6(D) does the jockey controller and pump count for no twist on (wire nuts) along with the wiring methods. Thanks
 

kwired

Electron manager
Location
NE Nebraska
Question on Art 695. Does 695.12(D) refer to only fire pump equipment or does the minimum height include wall heaters? Also 695.6(D) does the jockey controller and pump count for no twist on (wire nuts) along with the wiring methods. Thanks
I don't believe something like a wall heater is covered by anything in 695.

Pressure maintenance pumps aren't covered by 695 either (are specifically mentioned in 605.1(B) that they are not covered) other than mentioning that they are permitted to be supplied by same source, feeder, service possibly with conditions.
 