One of the install notes for this UPS mentions - UPS output ckts shall be installed in dedicated conduit systems and not shared with other electrical ckts. Unlike the other notes this one does not specify a section in the NEC.
The notes also mention UPS input and output conductors must be run thru separate conduits. Again - NEC section mentioned.
Can anyone comment on where I might find this to support the manual?? The UPS is for an industrial building for PLC loads.
The notes also mention UPS input and output conductors must be run thru separate conduits. Again - NEC section mentioned.
Can anyone comment on where I might find this to support the manual?? The UPS is for an industrial building for PLC loads.