blueheels2
Senior Member
- Location
- Raleigh, NC
- Occupation
- Electrical contractor
Have there ever been any big changed in the ampacity chart in the past 50 to 60 years?
I have a multifamily apartment where the underground feeder from the transformer to the meter mains failed last night. I have seen the wire in the main/pull box and in the transformer. Wire from the transformer is a single set of 500 AL (2 hots 1 neutral) that comes up through the slab into a junction box. A splice is made in that j/box splitting the 500/s into 2-500’s that land on a 60@ amp breaker.
Power Company (Duke) says that the cable is customer owned, customer problem.
However the wire from transformer to junction box is only rated for 310 amps current NEC. It’s interesting to me that in the j-box below the main they splice and make 2-500’s which would be good for the 600 amps, and send that to the breakers.
Makes me think the wire from transformer to junction box is Dukes wire and from the tap to the breaker is reallly the customers.
Plannning a complete replacement of the wire but due to the way things are wired I could never get parallel 500’s from the transformer to the junction box. Single 3” GRC leaves tap box and goes under the slab and stubs outside of the building footprint. Service is in a step down area slash 1/2 basement. No way to get there.
So am I right in thinking wire from transformer to j-box is under power company rules and from the j-box to the breaker is under NEC? Or when these were built (est 1965-1980) the NEC allowed a single set of 500 Al to feed a multi family dwelling ?
Sorr for the rambling post.
I have a multifamily apartment where the underground feeder from the transformer to the meter mains failed last night. I have seen the wire in the main/pull box and in the transformer. Wire from the transformer is a single set of 500 AL (2 hots 1 neutral) that comes up through the slab into a junction box. A splice is made in that j/box splitting the 500/s into 2-500’s that land on a 60@ amp breaker.
Power Company (Duke) says that the cable is customer owned, customer problem.
However the wire from transformer to junction box is only rated for 310 amps current NEC. It’s interesting to me that in the j-box below the main they splice and make 2-500’s which would be good for the 600 amps, and send that to the breakers.
Makes me think the wire from transformer to junction box is Dukes wire and from the tap to the breaker is reallly the customers.
Plannning a complete replacement of the wire but due to the way things are wired I could never get parallel 500’s from the transformer to the junction box. Single 3” GRC leaves tap box and goes under the slab and stubs outside of the building footprint. Service is in a step down area slash 1/2 basement. No way to get there.
So am I right in thinking wire from transformer to j-box is under power company rules and from the j-box to the breaker is under NEC? Or when these were built (est 1965-1980) the NEC allowed a single set of 500 Al to feed a multi family dwelling ?
Sorr for the rambling post.