700.10(D)(1)

Status
Not open for further replies.

m sleem

Top-notch Сasual Dating - Real-life Females
Location
Usa
Occupation
Health
In order to meet the code section, do we need to apply the same for the 13.8kv emergency cables, if needed what is the most appropriate assembly for 3x300mm2 cu/xlpe/pvc to be fire rated for 2hrs?
 
In order to meet the code section, do we need to apply the same for the 13.8kv emergency cables, if needed what is the most appropriate assembly for 3x300mm2 cu/xlpe/pvc to be fire rated for 2hrs?

Yes I believe so, it does not talk about voltage limitations in that section.
 