Greenboy
Member
- Location
- Seattle, WA
I am curious to learn regarding article 700.17. It is not clear to me if we meet the intent of this code article. We have (1) circuit feeding lights in a stairwell, from a emergency panel, downsteam from an life Safety ATS. The panel is on during normal power, and when power is disrupted, the generator kicks on, transfer switch switches to gen power, and within 10 seconds, the panel comes back on line.
My view is I meet the intent of 700.17(1). Therefore, I do not need to meet the intent of 700.17(2).
However, I have been reviewing on line, and it appears that I do not meet the intent of the code, with different interpretations of that code.
The inspector is telling me that I need (2) circuits feeding the area in case 1 circuit fails, and leave the area dark.
Please help
My view is I meet the intent of 700.17(1). Therefore, I do not need to meet the intent of 700.17(2).
However, I have been reviewing on line, and it appears that I do not meet the intent of the code, with different interpretations of that code.
The inspector is telling me that I need (2) circuits feeding the area in case 1 circuit fails, and leave the area dark.
Please help