Charlie,
The ROP and ROC for this issue are on line at NFPA as this was a 2005 code change. Here is the original proposal.
The ROP and ROC for this issue are on line at NFPA as this was a 2005 code change. Here is the original proposal.
13-135 Log #3034 NEC-P13
(700-28)
Final Action: Accept in Principle in Part
Submitter: Todd Lottmann St Louis, MO
Recommendation:
Add the following to Part VI of Article 700:
700.28 Selective Coordination.
All overcurrent protective devices in emergency systems shall be selectively coordinated to ensure proper isolation and localization of
a fault by the overcurrent devices closest to the fault condition and preventing loss of power to other unaffected parts of the emergency
system.
Substantiation:
The requirements contained in Article 700 focus on providing a reliable emergency system that will be operational when called upon
for its use as supported by the maintenance and testing requirements in 700.4. The critical nature of the dependence on emergency
systems for safety of human life, as stated in the scope, supports these requirements. This article specifically mandates that the
emergency circuits be separated from the normal circuits as shown in 700.9(B) and that the wiring be specifically located to minimize
system hazards as shown in 700.9(C), all of which reduce the probability of faults or failures to the system so it will be operational when
called upon. With the interaction of this article for emergency lighting for egress, it is imperative that the lighting system remain
operational in an emergency. Failure of one component must not result in a condition where a means of egress will be in total darkness
as shown in 700.16. In addition, the allowance to bypass the alternative source ground fault protection for equipment shows the
preference for system operation in the event of an emergency and the fact that if a fault occurs we do not want the whole system to go
down and create an unsafe situation for human life. Selectively coordinated overcurrent protective devices will provide a system that
will support all these requirements and principles. With properly selected overcurrent protective devices, a fault in the emergency
system will be localized to the overcurrent protective device nearest the fault allowing the remainder of the system to be functional as all
the previously mentioned requirements intend to do. Due to the critical nature of the emergency system uptime, selective coordination
must be mandated for emergency systems. This can be accomplished by both fuses and circuit breakers based on the system design and
the selection of the appropriate overcurrent protective devices.
Panel Meeting Action: Accept in Principle in Part
Delete 700.25 FPN and add New Section 700.28 to read as follows:
"700.28 Coordination. Emergency system(s) overcurrent devices shall be selectively coordinated with all supply side overcurrent
protective devices."
Panel Statement:
The panel agrees that selective coordination of emergency system overcurrent devices with the supply side overcurrent devices will
provide for a more reliable emergency system. By excepting in principle this proposal the FPN in Section 700.25 is no longer needed to
alert users about selective coordination. The part the panel accepts is selective coordination of emergency systems. The panel's wording
accomplishes the intent of the submitter without adding design aspects of selective coordination into this section.
Number Eligible to Vote: 14
Ballot Results: Affirmative: 13 Negative: 1
Explanation of Negative:
ELKINS: Perfectly selective coordination is not always possible for all fault current levels when protection is provided by common
molded case circuit breakers. This requirement will force the use of fuses which may expose workers to energized parts during
replacement or the use of more sophisticated breakers with complex settings which are more likely to be mis-set resulting in false trips.
Reliability and safety of these services are best served by the existing NEC FPN wording which alerts the user to the need for selectivity
when possible.