700 & 701 conductors

Status
Not open for further replies.

Rich Elec.

Senior Member
Location
Pennsylvania
I am questioning installing circuit conductors from a Art. 700 system and an Art. 701 system in the same raceway.
701.10 would allow it but, 700.10 prohibits it.
Am I correct that the 700.10 rule trumps 701.10, and that the conductors must be run in separate raceways?
 
I think you are correct. I see nothing in 700.10(B) 1 through 5 that would allow using the same raceway.
 