I am designing a 480VAC 700kW emergency gen (Art 700) with a remote raditor and EG room exhaust fans for combustion air. I am planning on tapping off the line side bus of the generator for the exterior remote radiator. The radiator uses a 15Hp motor at 22amps.
My question is what size should the conductors be off the EG bus to the 40amp OCPD?
Should I follow the tap rules in Art 240.21 and base it off the main OCPD of the generator (1200amps). Wire sized for 120amps to the OCPD. Or Can I just size the conductors for the radiator OCPD at 40amps?
Thanks for any help.