We are having an intense (yet fun) discussion in our office as to whether a generator with an auto transfer switch can be sized using 710.15(A) according to the 2020 code or if it must be sized according to article 702.4(B)
Argument A says that article 702 is obviously written specifically for generators and therefore is how they should be sized.
Argument B says that a generator can be sized according to 710.15(A) because
Argument A says that article 702 is obviously written specifically for generators and therefore is how they should be sized.
Argument B says that a generator can be sized according to 710.15(A) because
- 710.1 states, "... systems that operate in island mode... "
- Article 1 defines Island Mode as "The operational mode for... an isolated microgrid..."
- Isolated Microgrid is not defined in the 2020 NEC, but since the function of an ATS is to isolate the loads and create a micro-grid the system would be "operating in island mode".
- The informational note in 710.15(A) specifically calls out a generator as a part of a stand-alone system