705.11(B)(2)

msi99

Member
Location
Texas
Occupation
Solar
"(2) The service conductors connected to the power production source service disconnecting means shall be sized in accordance with 705.28 and not be smaller than 6 AWG copper or 4 AWG aluminum or copper-clad aluminum."

Does this imply that the conductors from the inverter to the interconnection point must be at least #6, irrespective of whether it is a line side tap or a load side back feed connection, even when the 75-degree and 90-degree calculations on 310.16 dictate the use of a smaller wire (for example, #8)?
 

jaggedben

Senior Member
Location
Northern California
Occupation
Solar and Energy Storage Installer
...

Does this imply that the conductors from the inverter to the interconnection point must be at least #6, irrespective of whether it is a line side tap or a load side back feed connection, even when the 75-degree and 90-degree calculations on 310.16 dictate the use of a smaller wire (for example, #8)?

No, it only applies to the line side of the service/PV disconnect.

All service conductors have the same requirement in article 230.
 