nsitzman
New User
- Location
- Tiffin, Iowa
- Occupation
- Building & Fire Code Official
I have one of Mikes older 2014 NEC videos covering PV connections bookmarked as it an excellent training video to brush up on interconnected sources when I feel rusty or a new question/interpretation comes up (
). I re-watched it yesterday as a question about the 120% rule for busbars came up in my jurisdiction. This topic is covered in the video (this starts at 55:25 in the video) under 705.12(D)(2)(3)(b) of the 2014 NEC, which still lives on as 705.12(B)(3)(2) in the 2020 NEC and states "Where two sources, one a primary power source and the other another power source, are located at opposite ends of a busbar that contains loads, the sum..."
The video does not show any load breakers on the busbar or feeders from the MLO panel to any loads, just the back-fed PV OCPD's, but this may be for clarity. The question that has come up in my jurisdiction is What constitutes a "load" for the purpose of this code section? Does this mean the 120% rule can not be applied if there are no breakers installed on this panelboard that serve 'active' loads? What if the only 'load' is a single pole circuit for a general purpose duplex receptacle off the side of the panelboard enclosure? Does the feeder from an MLO panelboard count as a "load" for the purpose of this code section even if there aren't breakers on the busbar? Does Mike have a newer video, or is there already a thread, that addresses this?
It seems that it might be splitting frog hairs to some, but words mean things. Sometimes the easy to overlook minutia in the NEC has a tremendous impact on correctly interpreting the code. With the new 2020 NEC requirements for the exterior disconnect, I see this becoming a more common occurrence/issue as installers are now using meter main type exterior panels as the norm rather than the exception. Thanks in advance for any direction on this!
Show less
REPLY
The video does not show any load breakers on the busbar or feeders from the MLO panel to any loads, just the back-fed PV OCPD's, but this may be for clarity. The question that has come up in my jurisdiction is What constitutes a "load" for the purpose of this code section? Does this mean the 120% rule can not be applied if there are no breakers installed on this panelboard that serve 'active' loads? What if the only 'load' is a single pole circuit for a general purpose duplex receptacle off the side of the panelboard enclosure? Does the feeder from an MLO panelboard count as a "load" for the purpose of this code section even if there aren't breakers on the busbar? Does Mike have a newer video, or is there already a thread, that addresses this?
It seems that it might be splitting frog hairs to some, but words mean things. Sometimes the easy to overlook minutia in the NEC has a tremendous impact on correctly interpreting the code. With the new 2020 NEC requirements for the exterior disconnect, I see this becoming a more common occurrence/issue as installers are now using meter main type exterior panels as the norm rather than the exception. Thanks in advance for any direction on this!
Show less
REPLY