• We will be performing upgrades on the forums and server over the weekend. The forums may be unavailable multiple times for up to an hour each. Thank you for your patience and understanding as we work to make the forums even better.

705.12(D)(2)(1)(3) -100% rated breaker exception needed

Status
Not open for further replies.

310 BLAZE IT

Senior Member
Location
NJ
This code section should account for 100% rated breakers being used.

690.9(B) has an exception for this, but 705 does not accommodate this.
690.8(B)(1) Has an exception for 100% rated breakers as well with similar language. I think this should be added here.

I also think wording for switchboard/switchgear should be added where applicable to (a) thru (d) since some of these sections clearly only apply to panelboards, while this code provision could be used on larger equipment.

As an example, I have 1440A of PV current, a 1600A 100% rated breaker, but yet I must account for 1800A on the bus which will not exist.
 

jaggedben

Senior Member
Location
Northern California
Occupation
Solar and Energy Storage Installer
I think you must mean 705.12(D)(2)(3).

I'm not sure I follow your reasoning. Several points:

- See 705.60(B) for the exception allowing use of a breaker rated for continuous 100% use.
- The 125% factor for continuous current is something that applies across the board to conductors, overcurrent devices and busbars (except as noted above). It has always accounted for current that doesn't exist. However the breaker rating(s) for inverters no longer play a part in the panelboard calculations as of the 2014 code. So unless the busbar is also 100% rated for continuous use I guess I don't follow the reasoning.
- The language in 705.12(D)(2)(3) does apply only to panelboards (for the entire section). You have perhaps a good point that by referring entirely to panelboards the code does not give guidance on switchgear and switchboards. But maybe for a project with an 1800A output one can budget for an EE to write a letter that will satisfy an AHJ that the installation is safe.
 

Carultch

Senior Member
Location
Massachusetts
It is worth mentioning that any 100% rated breaker you get will have to be mounted in it's own enclosure. You can't gang them up with other breakers.

Or possibly in a listed enclosure built for multiple 100% rated breakers. In any case, it is the enclosure as a whole and all products within it, that govern the 100% OCPD rating. It is not plug-and-play in an enclosure that contains standard breakers.
 
Status