wyeager
Member
- Location
- California
The figures below from SolarProfessional (Issue 7.3, Apr/May 2014) fairly closely illustrates a scenario I've been asked to evaluate under NEC 2014. In our case, however, there is a 200A switch with 50E main fuse on the subpanel instead of MLO. My question is whether or not the existing downstream OCPD satisfies 705.12(D)(2)(1)(b). My gut reaction is that the downstream OCPD needs to be right at the point of connection in order to protect the rest of the feeder (or that the feeder would need to be upsized as shown in figure 1). The other side of the argument is that the feeder (#2/0 Cu MV-105) can't be overloaded because the only loads on it are behind a 50E fuse (and then a 300kVA transformer).
Please let me know if I can provide further clarification and thanks in advance for your help.
William Ray Yeager, PE
Please let me know if I can provide further clarification and thanks in advance for your help.
William Ray Yeager, PE