708.10(C)(3) [third (3) following (C)]

Status
Not open for further replies.

fmtjfw

Senior Member
Section/Paragraph: 708.10(C)(3) [third (3) following (C)]

Revised Text

708.10 Feeder and Branch Circuit Wiring.
....
(C) COPS Feeder Wiring Requirements.
....
(3) Floodplain Protection.
Where COPS feeders are installed below the level of the 100-year floodplain, the insulated circuit conductors shall be listed for use in a wet location and be installed in a wiring method that is permitted listed for use in wet locations.

Substantiation

Requiring wiring methods to be listed for wet location is reasonable.

Listed for wet location is used in 300.50(B), 310.10(C)(3), 314.15, 330.10(A)(11)c., 366.6(A)(2), 366.120(2), 396.10(B)(2), Table 400.4 Note 9, 410.96, 547.5(C)(2), 547.8(C), 550.15(H), 725.179(E), and 760.179.