708 cops

Status
Not open for further replies.
On a design that I recently issued, the owner is considering changing one particular area into a COPS environment. I have tried to discourage that, since this is an existing area in a nearby building, rather than part of the new building, and therefore will need significant revisions in order to comply with 708. I haven't started that part of the design yet, since the client has not made their decision yet. But I am not expecting it to be an easy design process.
 
On a design that I recently issued, the owner is considering changing one particular area into a COPS environment. I have tried to discourage that, since this is an existing area in a nearby building, rather than part of the new building, and therefore will need significant revisions in order to comply with 708. I haven't started that part of the design yet, since the client has not made their decision yet. But I am not expecting it to be an easy design process.

So its my understanding that 708 is optional, and not required.
 
So its my understanding that 708 is optional, and not required.

708.1 Scope.
Critical operations power systems are those systems so classed by municipal, state, federal, or other codes by any governmental agency having jurisdiction or by facility engineering documentation establishing the necessity for such a system. These systems include but are not limited to power systems, HVAC, fire alarm, security, communications, and signaling for designated critical operations areas.
 
708 is optional just like 700 and 701 are. None of these come into play unless required by some other code or document.
 