TwoBlocked
Senior Member
- Location
- Bradford County, PA
- Occupation
- Industrial Electrician
Been reviewing 70E 2024. Was looking at table 130.7(C)(15)(a) Arc Flash PPE Categories for Alternating Current (ac) Systems.
There are division in the PPE Category depending on the available fault current of 25kA, 35kA, 42kA, and 65kA. I was taught long ago that you can determine the kA of a transformer by dividing the kVA by Z (impedance), divided y the V (voltage), wait is that right? I now understand that is not accurate, but seems the only reasonable rule of thumb when out in the field. That is, when there is a transformer that you can get to the nameplate.
But what about pole transformers? I am looking for a rule of thumb for determining the kA of pole transformers when out in the field. Maybe by the physical size or other characteristics like cooling fins?
And folks, I am not looking for "All I ever do is ... and it hasn't been a problem." type answers. OK?
There are division in the PPE Category depending on the available fault current of 25kA, 35kA, 42kA, and 65kA. I was taught long ago that you can determine the kA of a transformer by dividing the kVA by Z (impedance), divided y the V (voltage), wait is that right? I now understand that is not accurate, but seems the only reasonable rule of thumb when out in the field. That is, when there is a transformer that you can get to the nameplate.
But what about pole transformers? I am looking for a rule of thumb for determining the kA of pole transformers when out in the field. Maybe by the physical size or other characteristics like cooling fins?
And folks, I am not looking for "All I ever do is ... and it hasn't been a problem." type answers. OK?