We finally received a copy of the 2015 edition of NFPA 70E Hanbook. And surprise, surprise... it's still confusing!
130.5(C) states, "One of the following methods shall be used for the selection of PPE... The results of an incident energy analysis to specify an arc flash PPE Category in Table 130.7(C)(16) shall not be permitted"
However, Annex H seems to directly contradict this statement.
H.1 states, "Arc flash PPE categories may be applicable when using the incident energy method to perform an arc flash risk assessment. When performing an incident energy analysis, the arc flash labels created may include an arc flash PPE category."
Additionally, 130.5(D) states, "Available incident energy and the corresponding working distance, or the arch flash PPE category in Table 130.7(C)(15)(A)(b) or 130.7(C)(15)(B) for the equipment, but not both." when referring to the labels.
So one section tells me I cannot use an incident energy analysis to determine a PPE level, and another tells me it's ok. What am I misunderstanding here?
130.5(C) states, "One of the following methods shall be used for the selection of PPE... The results of an incident energy analysis to specify an arc flash PPE Category in Table 130.7(C)(16) shall not be permitted"
However, Annex H seems to directly contradict this statement.
H.1 states, "Arc flash PPE categories may be applicable when using the incident energy method to perform an arc flash risk assessment. When performing an incident energy analysis, the arc flash labels created may include an arc flash PPE category."
Additionally, 130.5(D) states, "Available incident energy and the corresponding working distance, or the arch flash PPE category in Table 130.7(C)(15)(A)(b) or 130.7(C)(15)(B) for the equipment, but not both." when referring to the labels.
So one section tells me I cannot use an incident energy analysis to determine a PPE level, and another tells me it's ok. What am I misunderstanding here?