mwm1752
Senior Member
- Location
- Aspen, Colo
Can someone describe a situation in detail in which condition 1 is not achieved. I seem to have a thought block looking for a wiring method not within the parameters of "a raceway or in metal-sheathed, metal-clad, non?metallic-sheathed, or Type UF cables"
725.136 Separation from Electric Light, Power, Class 1, Non?Power-Limited Fire Alarm Circuit
Conductors, and Medium-Power Network
(I) Other Applications. For other applications, conductors of Class 2 and Clas s 3 circuits shall be separated by at least 50 mm (2 in.) from conductors of any electric light, power, Class 1 non?power-limited fire alarm or medium power network-powered broadband communications circuits unless one of the following conditions is met:
(1) Either (a) all of the electric light, power, Class 1, non?power-limited fire alarm and medium -power network powered broadband communications circuit conductors or (b) all of the Class 2 and Class 3 circuit conductors are in a raceway or in metal-sheathed, metal-clad, non?metallic-sheathed, or Type UF cables.
(2) All of the electric light, power, Class 1 non?power-limited fire alarm, and medium-power network-powered broadband communications circuit conductors are permanently separated from all of the Class 2 and Class 3 circuit conductors by a continuous and firmly fixed nonconductor, such as porcelain tubes or flexible tubing, in addition to the insulation on the conductors.
725.136 Separation from Electric Light, Power, Class 1, Non?Power-Limited Fire Alarm Circuit
Conductors, and Medium-Power Network
(I) Other Applications. For other applications, conductors of Class 2 and Clas s 3 circuits shall be separated by at least 50 mm (2 in.) from conductors of any electric light, power, Class 1 non?power-limited fire alarm or medium power network-powered broadband communications circuits unless one of the following conditions is met:
(1) Either (a) all of the electric light, power, Class 1, non?power-limited fire alarm and medium -power network powered broadband communications circuit conductors or (b) all of the Class 2 and Class 3 circuit conductors are in a raceway or in metal-sheathed, metal-clad, non?metallic-sheathed, or Type UF cables.
(2) All of the electric light, power, Class 1 non?power-limited fire alarm, and medium-power network-powered broadband communications circuit conductors are permanently separated from all of the Class 2 and Class 3 circuit conductors by a continuous and firmly fixed nonconductor, such as porcelain tubes or flexible tubing, in addition to the insulation on the conductors.