Can a multiconductor 120V motor control circuit, i.e. TC-ER w/600V insulation, be routed in same cable tray with 300V ITC-ER instrumentation cable?
Can a multiconductor 120V motor control circuit, i.e. TC-ER w/600V insulation, be routed in same cable tray with 300V ITC-ER instrumentation cable?
Yeah. I’ve done a little more research; 300V and 600V can’t be run together in same conduit or cable tray unless there’s a barrier. 300V ITC cable can be used for 24VDC digital output signals i.e. PLC or DCS and other control applications that may fall into Class 1 circuitry.
Not sure how often that scenario would occur. PLC and DCS output signals are considered Class 1 circuits by default - even if they’re low energy- due to the Class 1 power supply, and therefore require 600V insulation. Unless of course ITC cable is used.
Can a multiconductor 120V motor control circuit, i.e. TC-ER w/600V insulation, be routed in same cable tray with 300V ITC-ER instrumentation cable?
Where are you getting that Class 1 circuits require 600V insulation?
Since TC-ER is a listed cable you can run anything with it including low voltage and communications. The fact that it carries 120V is irrelevant. So certainly you can run a ITC-ER cable with it in a cable tray.
-Hal
Hmm, that doc doesn't cite a code section for that.