I want to see if I am over thinking this one
725.48 Conductors of Different Circuits in the Same
Cable, Cable Tray, Enclosure, or Raceway.
Class 1 circuits
shall be permitted to be installed with other circuits as
specified in 725.48(A) and (B).
(A) Two or More Class 1 Circuits.
Class 1 circuits shall be
permitted to occupy the same cable, cable tray, enclosure, or
raceway without regard to whether the individual circuits are
alternating current or direct current, provided all conductors
are insulated for the maximum voltage of any conductor in the
cable, cable tray, enclosure, or raceway.
The way I read this is it is the maximum rated voltage of the conductors not what they are carrying. Example:
If you have a 120/240 feeder wire in conduit and it is THHN/THWN rated at 600v and you also pull in control wire with it, that wire must also have an insulation rating of 600v.
Am I over thinking this one?
725.48 Conductors of Different Circuits in the Same
Cable, Cable Tray, Enclosure, or Raceway.
Class 1 circuits
shall be permitted to be installed with other circuits as
specified in 725.48(A) and (B).
(A) Two or More Class 1 Circuits.
Class 1 circuits shall be
permitted to occupy the same cable, cable tray, enclosure, or
raceway without regard to whether the individual circuits are
alternating current or direct current, provided all conductors
are insulated for the maximum voltage of any conductor in the
cable, cable tray, enclosure, or raceway.
The way I read this is it is the maximum rated voltage of the conductors not what they are carrying. Example:
If you have a 120/240 feeder wire in conduit and it is THHN/THWN rated at 600v and you also pull in control wire with it, that wire must also have an insulation rating of 600v.
Am I over thinking this one?