725.51 and control cable amp correction Factors

Status
Not open for further replies.

Isaiah

Senior Member
Location
Baton Rouge
Occupation
Electrical Inspector
When applying correction factors per 725.51 to control cables if the amps exceeded 10% of the rating of the conductor you have to use 310.15(C)(1).
Say you had 10 control cables with just ONE circuit over the 10% of a #14Awg, (e.g 2Amps) you’d derate per the total of 10 current carrying conductors or 50%.....Or should it be if all 10 conductors carry +1.5A then you’d factor by 50%?


Sent from my iPhone using Tapatalk
 