Couldn’t figure out how to upload a picture from my phone, so hear me out. In my plant there is a feeder for a 2000A switchgear that doesn’t seem right. Here are the details.
Switchgear current load is only 480A.
Feeder is DLO installed in cable tray.
Three parallel runs of 777kcmil DLO, plus three 2/0 bare bonding conductors
Cable arrangement in tray goes:
Bond Red Black Blue Bond Red Black Blue Bond Red Black Blue
Single conductors are spaced 100% apart. The first bond is ty wrapped close to the edge of the tray, but the middle and last bonds are just ty wrapped in between the single conductor spacing between red and blue phases.
The resulting conditions result in approximately 22A on the first bond, 72A on the middle bond, and 52A on the last bond.
I cut the ty wraps on the middle bond, and pulled it out of the tray, away from the single conductors, and it dropped from 72A down to 10A.
Shouldn’t this installation have only one 250kcmil bonding conductor? This is a Canadian installation but our codes are very similar.
Switchgear current load is only 480A.
Feeder is DLO installed in cable tray.
Three parallel runs of 777kcmil DLO, plus three 2/0 bare bonding conductors
Cable arrangement in tray goes:
Bond Red Black Blue Bond Red Black Blue Bond Red Black Blue
Single conductors are spaced 100% apart. The first bond is ty wrapped close to the edge of the tray, but the middle and last bonds are just ty wrapped in between the single conductor spacing between red and blue phases.
The resulting conditions result in approximately 22A on the first bond, 72A on the middle bond, and 52A on the last bond.
I cut the ty wraps on the middle bond, and pulled it out of the tray, away from the single conductors, and it dropped from 72A down to 10A.
Shouldn’t this installation have only one 250kcmil bonding conductor? This is a Canadian installation but our codes are very similar.