I'm working off a spec for new service provided by companies in house electrician.
New 480V 1200-Amp service to gear with GFCI main breaker, now spec called out 3 runs of 500-MCM wire to feed from pole mounted transformer bank.
This works at 90*C but the spec provided just states breaker (1200A Adj, 3P [NGS 1200A Frame], Trip 1200 A, 310+, (4) 4/0-500 kcmil),
Dose not call out temp rating of connections and always been little confusing to me so i's always been taught to always size off 75*C unless it was a service where we crimped lugs on both ends of wire and bolted to bussing but then had to verify buss was good for 90*C so it was always standard to use 75*C
Since largest conductor on this breaker is 500 mcm i would need 4 runs of 350 MCM in 4 conduits to make this proper.
Ive had a few other post about transformers today from there spec and everything has been sized for 90*C not sure if person who wrote spec had a clue or im missing something between 75 and 90*C uses?
Thank you
New 480V 1200-Amp service to gear with GFCI main breaker, now spec called out 3 runs of 500-MCM wire to feed from pole mounted transformer bank.
This works at 90*C but the spec provided just states breaker (1200A Adj, 3P [NGS 1200A Frame], Trip 1200 A, 310+, (4) 4/0-500 kcmil),
Dose not call out temp rating of connections and always been little confusing to me so i's always been taught to always size off 75*C unless it was a service where we crimped lugs on both ends of wire and bolted to bussing but then had to verify buss was good for 90*C so it was always standard to use 75*C
Since largest conductor on this breaker is 500 mcm i would need 4 runs of 350 MCM in 4 conduits to make this proper.
Ive had a few other post about transformers today from there spec and everything has been sized for 90*C not sure if person who wrote spec had a clue or im missing something between 75 and 90*C uses?
Thank you