75*C vs 90*C

Status
Not open for further replies.

Vlietracer64

Member
Location
NYS
I'm working off a spec for new service provided by companies in house electrician.
New 480V 1200-Amp service to gear with GFCI main breaker, now spec called out 3 runs of 500-MCM wire to feed from pole mounted transformer bank.

This works at 90*C but the spec provided just states breaker (1200A Adj, 3P [NGS 1200A Frame], Trip 1200 A, 310+, (4) 4/0-500 kcmil),
Dose not call out temp rating of connections and always been little confusing to me so i's always been taught to always size off 75*C unless it was a service where we crimped lugs on both ends of wire and bolted to bussing but then had to verify buss was good for 90*C so it was always standard to use 75*C

Since largest conductor on this breaker is 500 mcm i would need 4 runs of 350 MCM in 4 conduits to make this proper.

Ive had a few other post about transformers today from there spec and everything has been sized for 90*C not sure if person who wrote spec had a clue or im missing something between 75 and 90*C uses?

Thank you
 
The person writing the spec is not acquainted with 240.4(C)
The only way it would be permissible would be if the terminated on a 90o breaker which is highly unlikely at 480v gear.
 
As Augie stated forget using the 90° C ampacity and calculate your conductors based on the 75° C ampacity. Since you're over 800 amps (no next standard size up rule) you'll need to meet or exceed the 1200 amp OCPD size with your conductors.
 
Looks like ill be submitting a corrected bid,
Got a call back and they stated im making it more complicated, their head of maintenance used to be a commercial electrician and knows what he's doing and another contractor already gave them pricing and didn't mention anything was wrong :happysad:
 
...their head of maintenance used to be a commercial electrician and "knows what he's doing" ...

Big deal. I used to be a commercial electrician, too, and I'm reading this thread so I can learn something about something outside of my expertise.

The typical commercial electrician couldn't design anything. They already have the plans and don't know enough to question them.
 
I see (often older) installations all the time that seem to use the "next size up" rule above 800 amps. I use to always think that they must have thought they could always use next size up, but that is a good point - maybe they were (incorrectly) using the 90 degree column for conductor sizing - never thought of that.
 
Same as you guys, i did commercial / industrial work for many years but its easy when your making wire pull and transformer connection off a designed, engineered stamped drawing
 
If this is a bid, I suggest you bid it the way it's shown and make sure your bid says per plans. Then, before signing a contract, hash it out.


Not so much of a bid as a in house design and build project they want pricing on, im going to re-work it and price it correctly and have a meeting with them this friday to discuss as it will not pass if built as per there current design
 
I'm working off a spec for new service provided by companies in house electrician.
New 480V 1200-Amp service to gear with GFCI main breaker, now spec called out 3 runs of 500-MCM wire to feed from pole mounted transformer bank.

This works at 90*C but the spec provided just states breaker (1200A Adj, 3P [NGS 1200A Frame], Trip 1200 A, 310+, (4) 4/0-500 kcmil),
Dose not call out temp rating of connections and always been little confusing to me so i's always been taught to always size off 75*C unless it was a service where we crimped lugs on both ends of wire and bolted to bussing but then had to verify buss was good for 90*C so it was always standard to use 75*C

Since largest conductor on this breaker is 500 mcm i would need 4 runs of 350 MCM in 4 conduits to make this proper.

Ive had a few other post about transformers today from there spec and everything has been sized for 90*C not sure if person who wrote spec had a clue or im missing something between 75 and 90*C uses?

Thank you

500 kCMIL AL or CU? How is it to be run? Buried in conduit underground? In a building ?
 
They Specked 500 MCM copper in conduit underground from utility pole to 1200-Amp Main breaker in outdoor 3R gear

3 - 4" comduits
4 500 mcm CU per conduit

Ampacity of 500kCMIL CU @ 75C 310.15(B)(16) = 380 Amps
Maximum Ambient temp of earth 30" deep (in my region) = 18.89 C
T310.15(B)(2)(a) adjustment @ 75C = 1.11
380 * 1.11 = 421.8 A
Adjust for 4 current conductors (Y system neutral counts) 310.15(B)(5) 421.8 * .8 = 337.44A
337.44 * 3 = 1012.31
Well its close but no go I'd say 1000A OCPD
If you did not have to count that neutral in the Y system you would be good.
 
Ampacity of 500kCMIL CU @ 75C 310.15(B)(16) = 380 Amps
Maximum Ambient temp of earth 30" deep (in my region) = 18.89 C
T310.15(B)(2)(a) adjustment @ 75C = 1.11
380 * 1.11 = 421.8 A
Adjust for 4 current conductors (Y system neutral counts) 310.15(B)(5) 421.8 * .8 = 337.44A
337.44 * 3 = 1012.31
Well its close but no go I'd say 1000A OCPD
If you did not have to count that neutral in the Y system you would be good.
110.14(C)(1) does not permit you to do that. It specifies the maximum conductor ampacity is the ampacity shown in Table 310.15(B)(16).
 
110.14(C)(1) does not permit you to do that. It specifies the maximum conductor ampacity is the ampacity shown in Table 310.15(B)(16).

Thanks Don good point I have always looked at 310.15(A)(2) Exception. Its interesting that 110.14(C)(1) ignores all the derating that might need to happen as well.
We always terminate a service lateral on a CT mounting base not a breaker like these:
CT mounting bases
Ill have to check the temp rating of the lugs on there.
Cheers
 