Are there other references about the use of Table 310.16?s 75? column besides 310.15(B) FPN(1)?
Thanks guy's, I wanted something more than a fine print note. I am questioning a design that includes parallel 350's with 600A OCP
This same design includes single 350's with 350AT/400AF OCP; I wonder what "AT" and "AF" stand for? Automatic Trip? Either way the 350's seem to barly comply with the AT but not the AF?
350 AmpTrip 400 AmpFrame BreakerThis same design includes single 350's with 350AT/400AF OCP; I wonder what "AT" and "AF" stand for? Automatic Trip? Either way the 350's seem to barly comply with the AT but not the AF?
I don't see a problem with parallel 350's from a 600A OCP. Parallel 350's is 620 Amps (without derating.) Unless maybe the parallel sets are installed in the same conduit.
310.16 75 degree column for 700kcmil = 460A, 240.4(B) = up to 500A. Am I missing something obvious?
310.16 75 degree column for 700kcmil = 460A, 240.4(B) = up to 500A. Am I missing something obvious?
Parallel 350 KCM are not equivalent to 700KCM. Very different because their is more surface area on two sets of 350 KCM. As David and others have said-- Look up the amps for 350KCM @ 75 C and double it.