75 degree ampacity of 310. 15(B)(16) and 240.4 (B) and 110.14 (C)

Status
Not open for further replies.

transman2

Senior Member
Location
Brooklet,Ga.
If I install a feeder for a sub panel with 500 AWG THHN wire (380 amps) using the 75 C allowable ampacities chart on 310.15(B)(16) and due to the fact that the breaker manufacture termination lugs are only rated at 75 degrees and following 110.14 (C),(a)(b). However 240.4 (B) says I am permitted to go the next higher standard overcurrent device rating which would be 400 amps. Is this a conflict?? Not sure how to rule on this and hope I can get some help. Thanks!!
 
500 kcmil copper THHN is rated for 380 amps @ 75° C as you've stated. As long as the calculated load is 380 amps or less you can use the next size up rule to get to the next standard size of 400 amps.
 
Last edited:
We also get lazy and forget to state the conductor ampacity cannot be greater than the 75°C column value or the adjusted and corrected ampacity, whichever is the lesser of the two.
 